If a roof has 900 square feet of horizontal attic surface and no vapor barrier, how many net free vent square feet are required?

Master the Florida Roofing Trade Exam with flashcards and multiple choice questions. Analyze hints and explanations for confident preparation and success.

Multiple Choice

If a roof has 900 square feet of horizontal attic surface and no vapor barrier, how many net free vent square feet are required?

Explanation:
Attic ventilation is based on a simple ratio: when there is no vapor barrier, you need net free vent area equal to 1/150 of the attic floor area. The horizontal attic surface here is 900 square feet, so 900 ÷ 150 equals 6. That means you must provide six square feet of net free vent area. If there were a vapor barrier, the requirement would be 1/300 of the attic area, which would be 900 ÷ 300 = 3 square feet—but with no vapor barrier, the correct amount is six square feet.

Attic ventilation is based on a simple ratio: when there is no vapor barrier, you need net free vent area equal to 1/150 of the attic floor area. The horizontal attic surface here is 900 square feet, so 900 ÷ 150 equals 6. That means you must provide six square feet of net free vent area.

If there were a vapor barrier, the requirement would be 1/300 of the attic area, which would be 900 ÷ 300 = 3 square feet—but with no vapor barrier, the correct amount is six square feet.